Looking for some help understanding what is happening here. Device is a Honeywell T6 Pro thermostat. Upon initial startup of Zwave-JS and issuing the first temperature setpoint - this sequence was observed. Later on subsequent temperature setpoints did not have this behavior - so this may be related to the first operation after network start? Looking for advice and error message interpretation. The sequence below seems to be:
Here is a sequence from later on that worked as expected
|
Beta Was this translation helpful? Give feedback.
Replies: 3 comments 8 replies
-
means there was a problem communicating with your controller (stick). In this case it didn't respond to any commands for a while. The problem is not related to the thermostat. |
Beta Was this translation helpful? Give feedback.
-
My conclusion on this issue is this:
I believe the root cause to be:
This occurs on two different systems, both using the Aoetec Gen 5 stick on a USB hub. The Synology NAS hardware is different 918+ and 720+ Rebooting the NAS, resetting the hub which had not be rebooted in a year did decrease the frequency of these errors significantly. |
Beta Was this translation helpful? Give feedback.
-
Here’s an example, I’m running 6_12_0 on two different systems Log from system 1
Log entry from system 2
|
Beta Was this translation helpful? Give feedback.
My conclusion on this issue is this:
I believe the root cause to be:
This occurs on two different systems, both using the Aoetec Gen 5 stick on a USB hub. The Synology NAS hardware is different 918+ and 720+
Rebooting the NAS, resetting the hub which had not be rebooted in a year did decrease the frequency of these errors significantly.