AqualinkD Web Page Controls Not Showing and Log Errors #369

Answered by sfeakes
CodeNoMore asked this question in Q&A
Discussion options

You must be logged in to vote

From that log, it looks like everything is working. You did stop and re-start AqualinkD though (I'm not sure why). So maybe you are not giving it long enough to start up and find all the data it needs. Remember PDA panels are very slow. And it will also take AqualinkD a long time to do anything with a PDA panel compared to RS. One thing I did notice from your different logs though, is I think you need to slow AqualinkD down to work better with the PDA panel.
Change the frame delay from 0 to 4 in aqualinkd.conf, that should help.

rs485_frame_delay = 4

Replies: 2 comments 6 replies

Comment options

You must be logged in to vote
1 reply
@CodeNoMore
Comment options

Comment options

You must be logged in to vote
5 replies
@CodeNoMore
Comment options

@sfeakes
Comment options

@CodeNoMore
Comment options

@sfeakes
Comment options

Answer selected by CodeNoMore