Replies: 4 comments 1 reply
-
The log shows the offset in brackets if offset is a positive value. The 1A telegram in offset 0: flowtemp, offset1: burnpower, Writing these values is temporary, the boier resets to default setting after ~3 minutes. So you have to repeat the commands every minute. That is what EM10 or thermostats do. In the 3.6 beta we have a scheduler where you can define such values. Create scheduler value with timer 00:01 and command |
Beta Was this translation helpful? Give feedback.
-
Amazing answer! So thank you again for bringing some light into the whole thing and how the EM10 works (sending every minute, I verified it already by watching "0x1A"). |
Beta Was this translation helpful? Give feedback.
-
Hello, we have a Logano Plus gb312, which has an EM10 module, which is actually supposed to provide the external specification of the performance. I have to check if that ever worked. Now the EM10 module is recognized, but no values are transferred via MQTT and I can also see it under the web interface. Are the values exclusively set? In other words, you can't see anything in the web interface. Or I have to add “customize”? My goal is to check the EM10 is configured correctly... the installer says "everything is fine, I have no idea why it doesn't work..." Thanks |
Beta Was this translation helpful? Give feedback.
-
But there is no burner set power on the MC10 (boilder), the boiler always runs at full power and does not regulate at all. I would like to see why the burner always runs at 100% and not only runs at 50% when set to 5 volts to the EM10 for example. That's why I thought you could see the external setpoint here |
Beta Was this translation helpful? Give feedback.
-
Hi All,
I have a Buderus GB162 boiler which is connected to a EM10 module. The EM10 module is used for telling the boiler either the set value of the flow temperature (°C) or the set value of the burner power (%).
When I run "watch on" and connect 5 V to the EM10 this gives these values for the set flow temperature:
[emsesp] alert(0x12) -W-> boiler(0x08), UBASetPoints(0x1A), data: 32
(for setting it to 50 °C)[emsesp] alert(0x12) -W-> boiler(0x08), UBASetPoints(0x1A), data: 00
(for setting it to off)That looks exactly the same for the set burner power:
[emsesp] alert(0x12) -W-> boiler(0x08), UBASetPoints(0x1A), data: 32
(for setting it to 50 %)[emsesp] alert(0x12) -W-> boiler(0x08), UBASetPoints(0x1A), data: 00
(for setting it to 0 %)I thought there's no way that the boiler can understand if it is % or °C requested so I was checking the raw packets ("watch raw"):
[telegram] Rx: 12 08 1A 00 00 11
(for setting the set flow temperature to "off")[telegram] Rx: 12 08 1A 01 00 13
(for setting the set burner power to "0 %")So there is a different offset (as expected) but this is only shown when displaying raw bytes.
Many questions for this topic:
Sorry guys if any of these questions are stupid but I'm brand new to EMS-ESP and I couldn't find any of these answered and also I couldn't find anything related to EM10 which surprised me since to my knowledge that's the official way of controlling the boiler from external systems.
Beta Was this translation helpful? Give feedback.