Your slave number is the Modbus number for the hardware that you are trying to reach on the Modbus line ( https://techcult.com/a-complete-guide-to-modbus-slave-principle/ For all of the above, as your PID is not in the supported hardware, you will need to read the user manual for your PID or contact the supplier) for questions. You can also inspire yourself from other hardware settings. As an example you can check the posts on my blog (here and here) for the Fuji PXF and MaxWell MTA PIDs. If you only nee the basic functions, check under which register your temperature value is (SV) and under which register you should put your set value or process value (PV). Nico |
Beta Was this translation helpful? Give feedback.
-
Roasters with TX4S often use 9600 baud, 8 bits, odd parity (O) with 1 stopbit or no parity (N) with 2 stopbits. Often the machines come with two PIDs, one configured as slave 1 and the other one as slave 2 holding there process value (PV) in register 1000 accessible via MODBUS function 4 in either C or F. Use Artisans channel 1 and 2 to assign those to ET and BT. Some deliver the data as is as uInt16, others as uInt16 with a factor 10 thus on the Artisan one needs to configure the dividier as 1/10. |
Beta Was this translation helpful? Give feedback.
-
I'm have an Autonics TX4S in my roaster connected vía USB to my Mac and want achieve to get here.
How do I configure the ports, the register number, function, decode, etc. According to my reader. I just need the basic readings for my roaster.
Beta Was this translation helpful? Give feedback.