Problem in sending topic to change LWT temp when cooling #62
Replies: 2 comments 3 replies
-
Hi @westminzer, thanks and greetings! I do not use cooling myself but I suspect that it may require the use of another parameter than "36 6"; perhaps it is just "36 7", but I would not recommend to just try writing to random parameter numbers. Instead, could you change the LWT temperature on the main Daikin controller while logging P1P2/R/#, and share the log or check the log for changes in the 00F036* messages? I would expect that you see one parameter change (or sometimes 2, or 4 parameters at the same time) in response to your manual action, and that parameter (or one of these) can then hopefully be used for setting LWT in cooling mode. |
Beta Was this translation helpful? Give feedback.
-
HA control is now available, so closing discussion here. |
Beta Was this translation helpful? Give feedback.
-
Hi all,
first of all a special greeting to Arnold. Some months ago I bought the P1P2 serial and now I'm finally able to control my Daikin Altherma 2 remotely through home assistant.
Everything works fine but I have a problem when I send a topic to change LWT set when in cooling mode. My pump is set to heat/cool with leaving water temp target (no room temp control). When I set it to "Heating" and, for example, I send "E 36 6 12C" target temp correctly changes to 30°C and all the ranges between 25°C to 60°C work. Otherwise, if it is set to cooling, and I send "E 36 6 A0" it should change to 16°C but actually nothing happens, I tried all the ranges from 8°C to 22°C with no result! Am I doing something wrong?
Hoping someone can help me.
Thank you :)